Subject:Re: Draft interconnection procedure
Cc:james.steffes@enron.com, christi.nicolay@enron.com
Bcc:james.steffes@enron.com, christi.nicolay@enron.com
Date:Thu, 15 Mar 2001 08:20:00 -0800 (PST)

As I mentioned over the phone, the general provisions of your tariff should
be modified so that they apply to generator interconnection (e.g., the
dispute resolution provision of the tariff currently only applies to
"Transmission Service" not interconnection service) Although I haven't done
a detailed review of PGE's tariff I noted similar concerns about Sections 6,
7.3, and 11. Also "transmission service" should be capitalized.

Some Other suggestions:

Preamble - Sentence three - delete: "[t]hese Interconnection Procedures do
not provide for transmission service on the Transmission System." Insert:
"These Interconnection Procedures apply only to the receipt point portion of
Transmission Service on the Transmission System."

Sentence four - delete "of the Transmission System" Parts II and III are
defined terms.

Section 2.2 - Under this provision, if the Interconnection Customer makes
changes to the information supporting its interconnection request that
"materially affect its interconnection" it can lose its place in the queue.
Given how much discretion this gives PGE, "materially affect" should be a
defined term or have a standard for its application.

Section 3.1: Revise the last sentence as follows "The Interconnection
Customer must execute, complete, and return . . . "

Further PGE should add a provision indicating that if its merchant function
desires interconnection that it should have to follow the interconnection
procedures.

Section 3.4 This section should be amended to require that the short circuit
and stability study take into consideration higher queued projects.

Section 3.4(iii): Power flow studies are only necessary for transmission
service not just for interconnection. Accordingly, Section (iii) should be
changed to have the information studied for the customer's information only
or to say that it is not related to the interconnection queue.

Section 4.1 - When does the customer's responsibility to respond to
higher-queued projects end? Does this extend the 60-day period every time it
happens?

Section 4.4

In sentence two - Delete "Network Upgrade necessary to remove overloads and"

Work the following definitions into Section 4.4:
Interconnection Facilities means the local equipment necessary to connect the
plant to the point of interconnection including increasing the capacity of an
existing local transmission line(s) to loop the lines into the plant in the
case where the capacity of the line is less than the capacity of the
generating plant under good utility practice.
Network Upgrades mean modifications beyond Interconnection Facilities
required for safe and reliable connection of the generating plant to the
utility system. They do not include transmission changes required to deliver
power beyond the point of interconnection.

In sentence three delete: modifications or additions to the Transmission
Provider's transmission lines and substations and add "Network Upgrades."

Proof-read and correct section numbers.



To: Mary Hain/HOU/ECT@ECT
cc: James D Steffes/NA/Enron@Enron, Jay_dudley@pgn.com
Subject: Re: Draft interconnection procedure

Comments:

2.3 Delete last sentence. If Enron is already in the queue (or
considered in a queue) before a TP's interconnection procedures are filed at
FERC, we don't want to have to resubmit something within 15 days in order to
remain in the queue. I don't think this is necessary and all are protected
because pre-existing requests will be posted on OASIS on the queue.

4.3 Enron has argued for 60 days consistent with the OATT times (lost
unfortunately). It may look odd for PGE to ask for 90 days. PGE is
protected because if it legitimately takes longer than 60 days, you send a
notification.

6 ((I realize that this language was included in CP&L, but recommend these
changes for PGE.)

6.1 Add after "as modified by the Commission" "if Customer chooses to
commence construction."
6.2 Modify last sentence -- The Agreement will provide milestones toward
placing the generator in service that the Interconnection Customer must make
reasonable progress toward or it will lose its queue priority (after
notification and opportunity to remedy.)

Thanks.



Mary Hain
03/13/2001 12:10 PM
To: Christi Nicolay
cc: James D Steffes/NA/Enron@Enron, Jay_dudley@pgn.com

Subject: Draft interconnection procedure

Since EPMI doesn't have any PGE interconnection requests pending, Jay Dudley
agreed to allow us to review PGE's draft FERC interconnection filing. As I
mentioned to you on Friday, PGE is trying to file this week so we have a
quick turn around time. I'm going to try to read it today.
---------------------- Forwarded by Mary Hain/HOU/ECT on 03/13/2001 10:09 AM
---------------------------
From: JAY DUDLEY/ENRON@enronxgate on 03/12/2001 07:39 PM CST
To: Mary Hain/HOU/ECT@ECT
cc: Frank Afranji/ENRON@enronxgate, MICHELE FARRELL/ENRON@enronxgate
Subject: Draft interconnection procedure

Mary - here is a draft of what the PGE interconnection procedure will be.
As I said, much of this is from VEPCO and Carolina Power.

Michele is redrafting it to be compatible with our OATT.

Let me know your comments as we want to file with FERC this week.

Thanks.

Jay.